Post by Gareth's was W7 now W10 Downstairs ComputerPost by SteveOn Mon, 1 Jul 2019 04:06:39 -0700 (PDT)
Post by sm_jamiesonHi all,
I'm finally running the cable to the garage.
What is the spacing for SWA cleats clipped to the side of a wall ?
SWA is 10mm x 3 core.
Thanks,
Simon.
One standard hammer's length.
AIUI, in a PME area, you must not export the PME Earth
but provide your own earth rod.
You can export your PME earth - but you must also make sure the
equipotential zone is exported with it.
So that means its only sensible to export it to places where its
possible to maintain the equipotential zone. (So you can't export it to
a place that has easy access to an independent earth like a greenhouse).
Also the earth in the submain will also need to double up as a main
bonding conductor, so the shield of the SWA alone will not usually have
a large enough "copper equivalent" cross section to act as a protective
earth and a main equipotential bond.
--
Cheers,
John.
/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/