Discussion:
Diverted neutral current
Add Reply
Scott
2024-12-23 12:56:44 UTC
Reply
Permalink
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.

What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Theo
2024-12-23 13:22:49 UTC
Reply
Permalink
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
Have a look at your incoming cable. If it has the earth wired to the sheath
of the cable that's TNS. If the earth goes into the neutral terminal that's
TNCS (or a PME sticker). If you have an outdoor earth rod that's TT.
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Yes. Particularly required on TT where the earth impedance can be 200 ohms
- the fault current wouldn't trip an MCB but it would trip an RCD. If next
door causes your earth to go live via the water pipe, your RCD won't help
but your earth bonding should shunt much of the current to your real earth.
On TT your neighbour should have an RCD that trips.

Theo
John Rumm
2024-12-23 16:16:14 UTC
Reply
Permalink
Post by Theo
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
Have a look at your incoming cable. If it has the earth wired to the sheath
of the cable that's TNS. If the earth goes into the neutral terminal that's
TNCS (or a PME sticker). If you have an outdoor earth rod that's TT.
Note that an earth rod can also be added to a TN-C-S install - it just
becomes another of the Multiple earths of PME.
Post by Theo
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Yes. Particularly required on TT where the earth impedance can be 200 ohms
- the fault current wouldn't trip an MCB but it would trip an RCD. If next
door causes your earth to go live via the water pipe, your RCD won't help
but your earth bonding should shunt much of the current to your real earth.
On TT your neighbour should have an RCD that trips.
If the neighbour has a disconnected neutral, but there is a path to your
neutral via theirs and yours equipotential bonding, then their RCD may
not see a fault since there will be a balance between live and what it
is seeing as neutral.
--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/
Scott
2024-12-23 17:00:28 UTC
Reply
Permalink
On Mon, 23 Dec 2024 16:16:14 +0000, John Rumm
Post by John Rumm
Post by Theo
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
Have a look at your incoming cable. If it has the earth wired to the sheath
of the cable that's TNS. If the earth goes into the neutral terminal that's
TNCS (or a PME sticker). If you have an outdoor earth rod that's TT.
Note that an earth rod can also be added to a TN-C-S install - it just
becomes another of the Multiple earths of PME.
Post by Theo
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Yes. Particularly required on TT where the earth impedance can be 200 ohms
- the fault current wouldn't trip an MCB but it would trip an RCD. If next
door causes your earth to go live via the water pipe, your RCD won't help
but your earth bonding should shunt much of the current to your real earth.
On TT your neighbour should have an RCD that trips.
If the neighbour has a disconnected neutral, but there is a path to your
neutral via theirs and yours equipotential bonding, then their RCD may
not see a fault since there will be a balance between live and what it
is seeing as neutral.
Would it not be safer to have an isolated section on the incoming
water pipe?
John Rumm
2024-12-23 21:43:58 UTC
Reply
Permalink
Post by Scott
On Mon, 23 Dec 2024 16:16:14 +0000, John Rumm
Post by John Rumm
Post by Theo
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
Have a look at your incoming cable. If it has the earth wired to the sheath
of the cable that's TNS. If the earth goes into the neutral terminal that's
TNCS (or a PME sticker). If you have an outdoor earth rod that's TT.
Note that an earth rod can also be added to a TN-C-S install - it just
becomes another of the Multiple earths of PME.
Post by Theo
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Yes. Particularly required on TT where the earth impedance can be 200 ohms
- the fault current wouldn't trip an MCB but it would trip an RCD. If next
door causes your earth to go live via the water pipe, your RCD won't help
but your earth bonding should shunt much of the current to your real earth.
On TT your neighbour should have an RCD that trips.
If the neighbour has a disconnected neutral, but there is a path to your
neutral via theirs and yours equipotential bonding, then their RCD may
not see a fault since there will be a balance between live and what it
is seeing as neutral.
Would it not be safer to have an isolated section on the incoming
water pipe?
Possibly, but were do you stop? Gas pipe, oil pipe, building metalwork,
that TT earth on an outbuilding submain etc. It is difficult to make
sure you catch all possible connections to an unintended earth.
--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/
Scott
2024-12-24 09:58:27 UTC
Reply
Permalink
On Mon, 23 Dec 2024 21:43:58 +0000, John Rumm
Post by John Rumm
Post by Scott
On Mon, 23 Dec 2024 16:16:14 +0000, John Rumm
Post by John Rumm
Post by Theo
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
Have a look at your incoming cable. If it has the earth wired to the sheath
of the cable that's TNS. If the earth goes into the neutral terminal that's
TNCS (or a PME sticker). If you have an outdoor earth rod that's TT.
Note that an earth rod can also be added to a TN-C-S install - it just
becomes another of the Multiple earths of PME.
Post by Theo
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Yes. Particularly required on TT where the earth impedance can be 200 ohms
- the fault current wouldn't trip an MCB but it would trip an RCD. If next
door causes your earth to go live via the water pipe, your RCD won't help
but your earth bonding should shunt much of the current to your real earth.
On TT your neighbour should have an RCD that trips.
If the neighbour has a disconnected neutral, but there is a path to your
neutral via theirs and yours equipotential bonding, then their RCD may
not see a fault since there will be a balance between live and what it
is seeing as neutral.
Would it not be safer to have an isolated section on the incoming
water pipe?
Possibly, but were do you stop? Gas pipe, oil pipe, building metalwork,
that TT earth on an outbuilding submain etc. It is difficult to make
sure you catch all possible connections to an unintended earth.
I regret to say that in the seasonal spirit of Christmas I watched
another 'JW' YouTube video last night and he actually said the best
way to install a TT system for an existing property is to use a
plastic water pipe. I think he also said that a plastic gas pipe can
be used outdoors but not indoors.
John Rumm
2024-12-24 10:15:28 UTC
Reply
Permalink
Post by Scott
On Mon, 23 Dec 2024 21:43:58 +0000, John Rumm
Post by John Rumm
Post by Scott
On Mon, 23 Dec 2024 16:16:14 +0000, John Rumm
Post by John Rumm
Post by Theo
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
Have a look at your incoming cable. If it has the earth wired to the sheath
of the cable that's TNS. If the earth goes into the neutral terminal that's
TNCS (or a PME sticker). If you have an outdoor earth rod that's TT.
Note that an earth rod can also be added to a TN-C-S install - it just
becomes another of the Multiple earths of PME.
Post by Theo
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Yes. Particularly required on TT where the earth impedance can be 200 ohms
- the fault current wouldn't trip an MCB but it would trip an RCD. If next
door causes your earth to go live via the water pipe, your RCD won't help
but your earth bonding should shunt much of the current to your real earth.
On TT your neighbour should have an RCD that trips.
If the neighbour has a disconnected neutral, but there is a path to your
neutral via theirs and yours equipotential bonding, then their RCD may
not see a fault since there will be a balance between live and what it
is seeing as neutral.
Would it not be safer to have an isolated section on the incoming
water pipe?
Possibly, but were do you stop? Gas pipe, oil pipe, building metalwork,
that TT earth on an outbuilding submain etc. It is difficult to make
sure you catch all possible connections to an unintended earth.
I regret to say that in the seasonal spirit of Christmas I watched
another 'JW' YouTube video last night and he actually said the best
way to install a TT system for an existing property is to use a
plastic water pipe. I think he also said that a plastic gas pipe can
be used outdoors but not indoors.
Yup plastic gas pipes outside are common in the distribution system, and
often right up to a premises these days, but less so after the meter on
the consumer side. Trackpipe (plastic coated corrugated steel) is quite
common though.
--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/
Andrew
2024-12-24 17:59:25 UTC
Reply
Permalink
Post by John Rumm
Post by Scott
On Mon, 23 Dec 2024 21:43:58 +0000, John Rumm
Post by John Rumm
Post by Scott
On Mon, 23 Dec 2024 16:16:14 +0000, John Rumm
Post by John Rumm
Post by Theo
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT).  I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
Have a look at your incoming cable. If it has the earth wired to the sheath
of the cable that's TNS. If the earth goes into the neutral terminal that's
TNCS (or a PME sticker). If you have an outdoor earth rod that's TT.
Note that an earth rod can also be added to a TN-C-S install - it just
becomes another of the Multiple earths of PME.
Post by Theo
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Yes.  Particularly required on TT where the earth impedance can be
200 ohms
- the fault current wouldn't trip an MCB but it would trip an
RCD.  If next
door causes your earth to go live via the water pipe, your RCD won't help
but your earth bonding should shunt much of the current to your real earth.
On TT your neighbour should have an RCD that trips.
If the neighbour has a disconnected neutral, but there is a path to your
neutral via theirs and yours equipotential bonding, then their RCD may
not see a fault since there will be a balance between live and what it
is seeing as neutral.
Would it not be safer to have an isolated section on the incoming
water pipe?
Possibly, but were do you stop? Gas pipe, oil pipe, building metalwork,
that TT earth on an outbuilding submain etc. It is difficult to make
sure you catch all possible connections to an unintended earth.
I regret to say that in the seasonal spirit of Christmas I watched
another 'JW' YouTube video last night and he actually said the best
way to install a TT system for an existing property is to use a
plastic water pipe. I think he also said that a plastic gas pipe can
be used outdoors but not indoors.
Yup plastic gas pipes outside are common in the distribution system, and
often right up to a premises these days, but less so after the meter on
the consumer side. Trackpipe (plastic coated corrugated steel) is quite
common though.
Up to the premises, but *never* inside the boundary of a building
including uninhabited spaces like garages. At least that is the
case with many of the semis where I live. These have a pair of
semi-detached garages in between each pair of houses but separated
from the houses by a metre wide path. The gas meter is in the garage
and the yellow plastic terminates under the concrete apron in front
of the up/over door and then a run of 3/4 inch iron pipe runs under
the garage floor to the meter. Another run of 3/4 inch iron runs
from the meter, under the path into the house entering adjacent to
where the Baxi Bermuda back boiler was originally fitted.
Andy Burns
2024-12-24 19:56:19 UTC
Reply
Permalink
Post by Andrew
Post by John Rumm
plastic gas pipes outside are common in the distribution system,
and often right up to a premises these days,
Up to the premises, but *never* inside the boundary of a building
including uninhabited spaces like garages.
As built, my house was plastic from the main in the footpath, to
"somewhere" in front of the house, then black iron rising in the
cupboard under the stairs where the meter was.

When Cadent replaced the main in the street they found the junction
between plastic and iron was under the built-on porch, so they had to
re-site the meter, coming up outside and in through the wall of the porch.

Then the meter and along the skirting in the hall a couple of feet, back
through the house wall into the garage along and then through the wall
again to under the stairs and rejoin my pipe that used to be on the
output side of the meter.

So externally it looks pretty clean, an 18" stub of white pipe up to a
plastic elbow (concealing a stopcock) and out of sight, I need to build
some sort of cupboard round the meter.

Not as bad as next doors, who have converted their garage, so it had to
go up, over the porch, along the flat roof, along the whole length of
the former garage, round to the back of the house ... looks awful!
Harry Bloomfield Esq
2024-12-25 11:29:01 UTC
Reply
Permalink
Post by Scott
I think he also said that a plastic gas pipe can
be used outdoors but not indoors.
Gas regulations! Plastic buried underground, is much less likely to be
melted by the heat from a fire, and less of an issue, even it it did. A
plastic gas pipe subjected to heat in a building, would be much more
serious.

David Wade
2024-12-23 13:30:14 UTC
Reply
Permalink
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
OK I believe that in reality there are only two systems in use, TT and
TN-C-S. Whilst your system may appear to be TN-S I understand you should
treat it as TN-C-S as any repairs to the distribution system may result
in Earth and Neutral being combined.
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
On PME Neutral and Earth are combined .....

Dave
Andy Burns
2024-12-23 14:18:08 UTC
Reply
Permalink
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD.
RCDs/RCBOs only care about an imbalance which is on your side of your
consumer unit, they won't trip due to a fault on the supplier's side.
John Rumm
2024-12-23 16:10:31 UTC
Reply
Permalink
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
Details of the types and how to tell which you have here:

https://wiki.diyfaq.org.uk/index.php/Earthing_Types
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD.
Indeed...

However (most) RCDs have no earth connection, so if it is the earth
which is introducing a potential into your house, the RCD won't see it,
and even if it tripped, it would not disconnect the earth.

(which is why we have equipotential bonding)
Post by Scott
I think I'll stick with
Morcambe and Wise before bed next time!
Bring me sunshine :-)
--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/
tony sayer
2024-12-23 23:59:04 UTC
Reply
Permalink
In article <vkc21n$199f6$***@dont-email.me>, John Rumm <***@n
owhere.null> scribeth thus
Post by John Rumm
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
https://wiki.diyfaq.org.uk/index.php/Earthing_Types
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD.
Indeed...
However (most) RCDs have no earth connection, so if it is the earth
which is introducing a potential into your house, the RCD won't see it,
and even if it tripped, it would not disconnect the earth.
John.. Do any RCD's have an earth connection i thought it was only the
very old e-RCD was it called?..
Post by John Rumm
(which is why we have equipotential bonding)
Post by Scott
I think I'll stick with
Morcambe and Wise before bed next time!
Bring me sunshine :-)
--
Tony Sayer


Man is least himself when he talks in his own person.

Give him a keyboard, and he will reveal himself.
Andrew Gabriel
2024-12-24 00:53:04 UTC
Reply
Permalink
Post by tony sayer
John.. Do any RCD's have an earth connection i thought it was only the
very old e-RCD was it called?..
Yes, some do. They can use it to trip on live/neutral reversal and
neutral disconnected. They can also use it to superimpose a low voltage
on the neutral wire. I'm racking my brains to remember why, but it might
have been to detect neutral/earth shorts even when no load is being
drawn. It was a standard feature of one of the RCD ICs.
--
Andrew Gabriel
Chris Green
2024-12-24 08:54:36 UTC
Reply
Permalink
Post by tony sayer
Post by John Rumm
However (most) RCDs have no earth connection, so if it is the earth
which is introducing a potential into your house, the RCD won't see it,
and even if it tripped, it would not disconnect the earth.
John.. Do any RCD's have an earth connection i thought it was only the
very old e-RCD was it called?..
ELCB - Earth Leakage Circuit Breaker
--
Chris Green
·
John Rumm
2024-12-24 10:24:55 UTC
Reply
Permalink
Post by Chris Green
Post by tony sayer
Post by John Rumm
However (most) RCDs have no earth connection, so if it is the earth
which is introducing a potential into your house, the RCD won't see it,
and even if it tripped, it would not disconnect the earth.
John.. Do any RCD's have an earth connection i thought it was only the
very old e-RCD was it called?..
ELCB - Earth Leakage Circuit Breaker
Yup earth connection for those is the whole MO, a different approach to
fault detection:

https://wiki.diyfaq.org.uk/index.php/ELCB

not to be confused with those current operated RCDs that also have earth
for detecting things like polarity reversal and other fault conditions.

(oddly, those makers that produce them, seem rather shy on promoting the
benefits / features)
--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/
John Rumm
2024-12-24 10:20:22 UTC
Reply
Permalink
Post by tony sayer
owhere.null> scribeth thus
Post by John Rumm
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
https://wiki.diyfaq.org.uk/index.php/Earthing_Types
Post by Scott
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD.
Indeed...
However (most) RCDs have no earth connection, so if it is the earth
which is introducing a potential into your house, the RCD won't see it,
and even if it tripped, it would not disconnect the earth.
John.. Do any RCD's have an earth connection i thought it was only the
very old e-RCD was it called?..
You quite often see it on some brands of RCBO for example:

https://mksentrycircuitprotection.co.uk/product-item/residual-current-breakers-with-overcurrent-protection-rcbos/
--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/
tony sayer
2024-12-23 23:56:57 UTC
Reply
Permalink
Post by Scott
As a distraction from all the Christmas stuff, I watched John Ward's
YouTube video on diverted neutral current last night. I just about
followed the explanation about the three earthing systems (TN-S,
TN-C-S and TT). I am now wondering if there is an easy way to find
out which system I have, bearing in mind John's admonition not to take
anything apart. It is quite alarming to think I could encounter 230
volts in my tap next time I take a shower because of a fault in next
door's wiring.
What about an RCD? I thought the RCD/RCBO measured any difference in
current between the 'brown' and the 'blue' and therefore any leakage
to earth would immediately trip the RCD. I think I'll stick with
Morcambe and Wise before bed next time!
Very simply an RCD looks at the current in on the Live wire and out on
the neutral if there is an unbalance caused by the incoming live being
diverted elsewhere then once its tripping rating is exceeded then out it
goes and will disconnect Both lines so in effect your isolated.

Unless you share the same earth rod or wire with someone else then that
can be a bit iffy;!.

Course on a more of less normal supply the earth and neutral are bonded
at the substation ..
--
Tony Sayer


Man is least himself when he talks in his own person.

Give him a keyboard, and he will reveal himself.
Loading...